Door strike not energizing upon pressing door release switch

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Door strike not energizing upon pressing door release switch
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • Tom_Poovey
    Tom_Poovey
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1313 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Door strike not energizing upon pressing door release switch

Picard Product_Support
‎2018-09-07 12:32 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 01:11 AM

Issue

The door strike will not energize upon pressing door release switch.

Product Line

TAC INET

Environment

  • I/NET DPU
  • SCU

Cause

Multiple Possible Causes -

  • Programming Error
  • Wiring Error

Determine Cause

  1. Have someone watch the DPU or SCU while you press the exit button.  You should see an LED light come on beside the Lock relay. 
  2. If you do, then you have a wiring issue.
  3. If you do not, then you have programming issue.

Resolution

If you have a Wiring Error

  1. Do not assume that because it worked before the wiring is correct
  2. Check the voltage on the lock power supply
  3. Consult the appropriate TCON to determine that the wiring for the exit button is correct
  4. Disconnect the wiring from the DPU/SCU and use a continuity meter to ensure that the exit button is functional.
  5. Hard wire the strike to remain unlocked and check that the door can be opened. (if not, repair door hardware)

If you have a programming Error

  1. Connect to the correct controller
  2. Select Edit > Controller > Doors
  3. Modify the affected door
  4. Ensure that the Door Strike Parameter is set to "Both"
  5. Ensure that the Door Release switch is set to either Normally Open or Normally closed
  6. Ensure that the Strike Duration is long enough to allow a user to press the exit button and still have time to exit the door.
  7. Click OK
  8. Select Edit > Summary > Controller
  9. Ensure that no door points are in manual control
  10. Consult the appropriate TCON to ensure no internal points are taking up needed point addresses.
  11. Re-test the door.
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 1638
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of