Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Does the Niagara R2 Modbus driver support a 6-digit address format?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Does the Niagara R2 Modbus driver support a 6-digit address format?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4315 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Does the Niagara R2 Modbus driver support a 6-digit address format?

Picard Product_Support
‎2018-09-06 02:28 PM

Last Updated: Administrator CraigEl Administrator ‎2023-10-16 03:38 PM

Issue

Does the Niagara R2 Modbus driver support a 6-digit address format?

Product Line

TAC IA Series

Environment

Niagara R2 Modbus driver

Cause

Modbus 6 digit addressing is not supported when using modbus format in the driver.

Resolution

The six-digit address format and the five-digit format are just two different notations for the same thing - there is no difference in the protocol. For example, the first one thousand holding registers are normally represented as:
(modbus) 40001 to 49999 -or- (decimal) 0 to 9998 -or- (hex) 0 to 270E

When using modbus format in the driver, the left most digit, '4' in this example, is part of a convention that indicates the 'type' of point and, when using that convention, the point type does not have to be specified.  For example, for modbus point 40001 the '4' indicates that it is a holding register.

But there are actually 64000 holding registers available and, using the common 5-digit modbus notation, it is not possible to specify more than 9999 of them. The six digit convention just moves this 'type' digit one space to the left.

In this six-digit notation, the first one thousand holding registers would be 400001 to 409999. This 6-digit convention for 'modbus' formatted addressing is not supported but it is still possible to use decimal or hex notation to specify these addresses with Niagara R2.

When 'modbus' formatted addresses are used, the driver subtracts 1 from the entered address, since modbus uses base 1 formatting and decimal uses base 0.  When using decimal or hex, the leading digit is dropped and subtract one from the register value and optionally convert to hex and use that as the point address.

For example, to read data from register address = 422202

Drop the leading character = 22202

Subtract 1 = Decimal address 22201 or hex address 56B9

Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 3894
  • CraigEllis23
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore