Does the Modbus XDriver interface with the ATV212 speed drive?
  • Does the Modbus XDriver interface with the ATV212 speed drive?
  • AdamSteele
    AdamSteele
‎2018-09-11 06:16 AM
Continuum
Modbus XDriver
Unable to get Modbus RTU communications working with the ATV212 drive.
Unfortunately, this does not work. The Modbus XDriver's cannot reference the large number address range that the ATV212 uses (above 64,000).
A workaround for this would be to use the BACnet MSTP interface available on the ATV212 to establish communications.
  • 14459