Does CyberStation meet BACnet specification Annex J?
  • Does CyberStation meet BACnet specification Annex J?
  • BillNeville
    BillNeville
‎2018-09-06 12:42 PM
A project specification requires compliance with BACnet Specification Annex J. Is Continuum compliant?
CyberStation B-OWS
bCX
A project specification has the following in it:
Operator Workstation: Provide operator workstation that complies with Annex J of the BACnet specification for IP connections. This device shall use Ethernet to connect to the IP internetwork, while using the same Ethernet LAN for non-IP communications to other BACnet devices on the LAN. Workstation shall support Foreign Device Registration to allow temporary workstation connection to IP network.
This is saying the BACnet workstation (B-OWS) must communicate to both BACnet IP devices and BACnet MSTP devices. CyberStation communicates over IP to BACnet IP devices and through a bCX or other BACnet gateway to the BACnet MSTP devices.
CyberStation does support Foreign Device Registration.
CyberStation does meet this specification.
  • 7277