Does Continuum support using a CSV file import to create object types other than Personnel objects?
  • Does Continuum support using a CSV file import to create object types other than Personnel objects?
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 01:47 PM
Can you import a csv file to create infinity controllers.
CyberStation
Personnel Objects
CSV
Excel
To create objects in Continuum by importing a text file.
A CSV import file can be used to create objects of most classes.
The CSV file must contain the at least three lines
  • A line establishing the class of the objects that are to be created
  • A header line describing the order of the attributes in subsequent lines with each attribute name separated by a comma.
  • A line stating the value of each attribute separated by a comma.
If objects of more than one class are created a new section of the CSV file must be created beginning with the objects class.
  • 5251
0% helpful (0/1)