Issue
Product Line
TAC IA SeriesEnvironment
- Niagara R2
- MNL Controllers
Cause
When Authentication is enabled in the LonWorks service without proper commissioning, MNL controllers can enter one of two states:
- Recoverable Mode – Authentication enabled but controllers not commissioned with Authentication.
- Permanent Hard Offline Mode – Authentication cleared via service pin, then recommissioned incorrectly, making the controller unrecoverable.
Resolution
- Do NOT enable Authentication when MNL controllers are present on the LON trunk.
- If Authentication was enabled:
- Use the service pin method to clear controller authentication (refer to WorkPlace Tech Tool 4.0 Engineering Guide, p. 602).
- Attempt recovery using NodeUtil to access and modify memory. Contact Product Support for detailed instructions.
- If the controller was recommissioned after clearing authentication, it will be permanently offline and cannot be recovered.