Issue
The "Display on alarm" feature for the Alarm view object does not display when the Alarm is triggered. This occurs even though the checkbox is checked, as shown below.
Product Line
EcoStruxure Building Operation
Environment
Building Operation Workstation
Cause
When the user is logged in with a Workspace view that does not show any Alarm viewers, no alarms are presented to the Workspace; hence the "Display on alarm" function does not load. This is as intended. An example of this type of Workspace would be the Administration Workspace which presents no alarms to the user while they are using this Workspace.
Resolution
For the Alarm view to "Display on alarm", it is necessary to add the Alarm Pane to the Workspace (as shown below) or use a Workspace view with the Alarm Pane included.