Issue
Exported PE program from SX8000 and imported into Continuum but the PE program will not compile in Continuum
Error: Total number of characters used in line labels exceeded maximum.
Product Line
Andover Continuum
Environment
- CyberStation
- All CX controllers
- All i1 controllers
- All b3 controllers
Cause
Difference in PE program line labels limits between Infinity and Continuum.
Resolution
There is a slight difference in line labels limit between Infinity and Continuum, the PE program is exceeding the line labels limit for Continuum, eliminate some line labels to make the PE program compile.
See Plain English program limitations on number of characters in program and line labels for PE programs limits in Continuum.