Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Xdriver enabled options on Net controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Xdriver enabled options on Net controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterEdvik
    PeterEdvik
  • Dave_Shore
    Dave_Shore
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • JohnBoehmer
    JohnBoehmer

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3031 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Xdriver enabled options on Net controller

Picard Product_Support
‎2018-09-11 06:24 AM

Last Updated: Janeway PeterEdvik Janeway ‎2022-08-30 10:18 PM

Issue

How can I determine which comm port on my Infinity Controller has been Xdriver enabled.

Product Line

Andover Continuum

Environment

  • Infinity Controller CX9900 (NC), CX9980 (NC2), bCX9640, bCX4040, ACX5720 ACX5740
  • XDriver, x-driver

Cause

Need to determine if the comm port(s) on a controller are XDriver enabled.

Resolution

View the controller options page in CyberStation or from the controllers webpage. 

NC2 (NCII, NetController 2, CX9680)
Option tab - example NC2
Xdriver Comm1 : 00000009 (0000)  (XDriver enable and but not loaded)
Xdriver Comm2 : 00000000 (0000)  (XDriver not enabled)
Xdriver Comm3 : 00000000 (0000)  (XDriver not enabled)
Xdriver Comm4 : 00000000 (0000)  (XDriver not enabled)
 

bCX bCX9640 bCX4040 - NOT bCX4000
The bCX has two comms ports, the XDriver functions can be enabled on none, either or both at the time of ordering (add X1, X2 or X12)
Option tab - example bCX
Xdrvr Comm1:00000009 (DF23)  (XDriver enable and loaded)
Xdrvr Comm2:00000000 (0000)  (XDriver not enabled)

ACX ACX5720 ACX5740
The ACX57x0 has a single comm port, the XDriver functions can be enabled at the time of ordering (see the
Option tab - example ACX57
Xdriver Comm1 : 00000009 (0000)  (XDriver enable and but not loaded)

NOTES

  • (00000000=XDriver not enabled, 00000001=CommPort only, 00000009=CommPort & Ethernet enable)
  • The four digit number in bracket shows which Xdriver is load and corresponds to "Xdriver valid" at the bottom of the xdriver.xdr file.
  • If Ethernet support is required on the port then this should be requested at the time of ordering.
  • XDrivers like Modbus TCP/IP and Bacnet IP are loaded on to a comms port but communicate via the Ethernet port, therefore the XDriver Ethernet support needs to be enabled for these XDrivers to operate.
Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 7962
  • DavidShore22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of