Defining what port is used for the I/A Series G3/N4 LON and Serial tunnel clients

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Defining what port is used for the I/A Series G3/N4 LON and Serial tunnel clients
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • WaynePeters
    WaynePeters
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1839 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Defining what port is used for the I/A Series G3/N4 LON and Serial tunnel clients

Picard Product_Support
‎2018-09-06 12:08 PM

Last Updated: Guinan RandyDavis Guinan ‎2022-02-17 12:46 PM

Issue

What port is used for the I/A Series G3/N4 LON and Serial tunnel clients and can it be changed?

Product Line

TAC IA Series

Environment

  • I/A Series G3/N4 Enterprise Server
  • I/A Series G3 ENC
  • I/A Series Jace 8000

Cause

Requires port change due to routing or firewall conditions.

Resolution

By default, the G3/N4 Tunnel Service utilizes TCP port 9973. The port used for tunneling can be configured by modifying the Server Port within the tunnel service properties.

Example: Configuring the Lon tunnel server

In the palette sidebar, open the lontunnel palette.

Open the ENC/JACE station and expand its Services folder.

  • If no TunnelService exists, paste one from the palette into the Services folder.
  • If a TunnelService does exist, go to the next step.

Note: Only one TunnelService is needed in a station's services, and it can hold multiple tunnel components (both LonTunnel and (serialTunnel). The TunnelService in the lontunnel module is identical to the TunnelService in the (serial) tunnel module.

From the palette, paste a LonTunnel under the station's TunnelService

The station should now have a TunnelService and a child LonTunnel component. Configure the properties and modify the TunnelService server port if required.

Note: If the ENC/JACE has multiple LON ports (and corresponding LonNetworks), the same number of LonTunnel components can be copied under the TunnelService. Each LonTunnel component can then be associated with a particular LonNetwork (by its LONn device name).

For any station user that needs to Lon tunnel, make sure the user has admin write permissions for the LonTunnel(s).

Example: Configuring the serial tunnel server

In the palette sidebar, open the tunnel palette.

Open the ENC/JACE station and expand its Services folder.

  • If no TunnelService exists, paste one from the palette into the Services folder.
  • If a TunnelService does exist, go to the next step.

Note: Only one TunnelService is needed in a station's services, and it can hold multiple tunnel components (both LonTunnel and (serialTunnel). The TunnelService in the lontunnel module is identical to the TunnelService in the (serial) tunnel module.

From the palette, paste a SerialTunnel under the station's TunnelService.

The station should now have a TunnelService and a child SerialTunnel component.

In the SerialTunnel's property sheet, expand the "Serial Port Config container."

Enter the COMn "Port Name" used by the target driver network, and specify other parameters as defined in the network's configuration.

If the ENC/JACE has multiple serial-type driver networks (and corresponding COM ports), the same number of SerialTunnel components can be copied under the TunnelService. Each SerialTunnel component can be associated with a particular network (by its COMn port name) and set the other parameters accordingly.

For any station user that needs to the serial tunnel, make sure the user has admin write permissions for the SerialTunnel(s).

Labels (1)
Labels:
  • TAC IA Series
Tags (4)
  • Find more articles tagged with:
  • 8330
  • Jace 8000
  • n4
  • RandyDavis22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore