Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Data Sync Service stops working

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Data Sync Service stops working
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • AdamSteele
    AdamSteele

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4153 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Data Sync Service stops working

AdamSteele Champion
‎2019-07-25 02:36 AM

Issue

Security Expert and Security Expert Data Sync Service are running and operational. After a while, the Data Sync Service stops synchronizing. Reviewing the Data Sync Service log file indicates that the connection was lost and that the operator username or password are incorrect.

[WARN ] [0    ] - Failed to get Operator where ID = 6. Error Code: 8 (Connection lost/not logged on)
[ERROR] [0    ] - Incorrect username or password, or the operator does not have access. Error Code: 0 (Error).


Restarting the entire system or the Security Expert Data Service resolves the problem.

Product Line

EcoStruxure Security Expert

Environment

  • Multiple Security Expert Clients
  • Security Expert Data Sync Service

Cause

The number of concurrent clients has exceeded the licensed limit.

 

The Data Sync Service will make a connection each time it synchronizes and then close that connection when finished. If there are no client licenses available for it to use when attempting to connect then it will fail and present the following events in the log file.

[INFO ] [0    ] - Verifying product license information...
[WARN ] [0    ] - Failed to get Operator where ID = 6. Error Code: 8 (Connection lost/not logged on)
[ERROR] [0    ] - Incorrect username or password, or the operator does not have access. Error Code: 0 (Error).
[INFO ] [0    ] - Next sync will begin at 24/07/2019 9:42:59 AM


Each Security Expert Client connection will take up a client license. If the SSN is enabled for three concurrent client connections this will allow for two Security Expert Clients and one Data Sync Service.

Resolution

  1. Purchase more client licenses (SX-CLNT) for the sites SSN.
  2. Ensure that no more than [one less than the maximum concurrent clients number] Security Expert Clients are running when the Data Sync Service is also running.
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (3)
  • Find more articles tagged with:
  • AdamSteele19
  • AdamSteele20
  • AdamSteele26
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore