DPU Restore, what triggers this operation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • DPU Restore, what triggers this operation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • sesa139513
    sesa139513
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1436 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

DPU Restore, what triggers this operation

Picard Product_Support
‎2020-09-17 06:28 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2020-09-17 06:31 PM

Issue

DPU Restore, when and what information is downloaded to the Door Controllers

Product Line

TAC INET

Environment

  • TAC I/Net Seven site with DPU or SCU
  • 7910, 7920 1284, 1280 door controllers, download

Cause

A variety of errors with door access can be attributed to download individual information to the door controller(s).

Resolution

When changes are made to any one of the following, a download is triggered to each of the DPU/SCU controllers.

  • Name
  • Group
  • Issue Level
  • Card Number

If using DPU Restore, remember that during the DPU\SCU restore, these are the items that are being downloaded.

  1. Cold Start signal - followed by point data from the SLI
  2. Tamper Parameters (SCU Only)
  3. Translation parameters
  4. Tenant information
  5. Floor Mapping\Personnel data for each Elevator\Door
  6. Secondary Time Schedules
  7. End of the Cold Start process
  8. After the Cold Start ends, then the Big Card Numbers (HEX) are restored from the SLI to the DPU\SCU controllers
Labels (1)
Labels:
  • TAC INET
Tags (2)
  • Find more articles tagged with:
  • 4053
  • RobertAndriolo20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of