Issue
The desktop shortcut created during the installation of DMS OPRIF 11.6 for DCT does not work as expected.
Product Line
TAC IA SeriesEnvironment
DMS OPRIF 11.6 running in a Windows OS.
Cause
The installed shortcut incorrectly calls c350dct instead of the required batch file dct.bat. This prevents the DCT tool from launching properly.
Resolution
-
Run DCT Manually
- Navigate to the DCT folder and run
DCT.BATdirectly.
- Navigate to the DCT folder and run
-
Modify Desktop Shortcut
- Edit the shortcut target line from:
to:call c350dctcall dct.bat
- Edit the shortcut target line from:
-
Improve Performance
- Open
DCT.BATin the DCT folder and change:
to:dctgl.exe %1 %2start /low dctgl.exe %1 %2 - This runs the process with lower priority, improving system responsiveness.
- Open