DMS-350A Battery Does Not Charge After Replacement
  • DMS-350A Battery Does Not Charge After Replacement
  • CraigEl
    CraigEl
  • sesa119747
    sesa119747
‎2018-09-06 02:31 PM
Last Updated: Administrator CraigEl Administrator ‎2025-11-19 08:02 PM
Two new batteries were installed in a DMS-350A panel, but neither charged to the point of indicating GOOD. The voltage measured at the battery clips with the battery installed reads approximately 4.5 VDC.
TAC IA Series
DMS-350A
Poor physical connection between the battery and the battery holder contacts prevents proper charging.
  1. Inspect Battery Holder Contacts
    • Check for dirt, corrosion, or misalignment on the contacts.
  2. Clean Contacts
    • Use a suitable contact cleaner or a lint-free cloth to remove debris.
  3. Adjust Contact Position
    • Gently bend the battery holder contacts to ensure a firm and secure connection with the battery terminals.
  4. Verify Voltage
    • After adjustment, confirm that the battery voltage rises above 4.5 VDC and eventually indicates GOOD status.
  • TAC IA Series
Tags (2)
  • 3719
  • CraigEllis25
