Cyberstation online help
The highlighted text in the Workstation Time Tab online help is inaccurate.
Note: When entering this number, use the opposite sign (negative or positive) from what you actually want the system to write. For example, if you are 300 minutes (5 hours) ahead of GMT, enter:
-300
For example, if you are -240 minutes (4 hours) behind GMT, enter:
240
Under UTC Offset, the Note should read as follows:
Note: When entering this number, use an negative integer to specify time zones to the West (earlier than) Greenwich Mean time and a positive integer to specify time zones that are to the east of GMT.
-300
For example, if you are 240 minutes behind (later than) GMT, enter:
240