Issue
When alarm is triggered in the controller sometime the alarm will immediately be displayed on the Alarm View as expected, you trigger the same point alarm a few times and some times there is a delay of up to a minute or two before the alarm shows up on the Alarm View.
Looking at a list view of the alarms you can see the difference between the time stamp and the time of log
Product Line
Andover Continuum
Environment
- CyberStation
- All controllers
Cause
The controller has been taught about CyberStation whose network ID has been since changed.
Resolution
Use a PE program to find out from the controller's perspective what it has been taught. If the contr...