Creating an alarm to show when a controller output HOA is not in the Auto position.
  • Creating an alarm to show when a controller output HOA is not in the Auto position.
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 11:02 AM
Can an alarm be created to notify an operator when the HOA switch on a controller is no longer in the Auto position?
Is it possible to show on a graphic when a controller output is not in the Auto position?
  • Output
  • Override
  • Alarm
Controller HOA switch security.
Each output has an Override attribute which is set to True when controllers corresponding HOA switch is not in the Auto position.
The Override attribute can be used for alarming and for a visual indication on a Pinpoint graphic.
  • 11352