Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Creating an Extended Trend Log for b3 (Infinet i1/i2) Point and Value Logs

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Creating an Extended Trend Log for b3 (Infinet i1/i2) Point and Value Logs
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • Dave_Shore
    Dave_Shore
  • BillNeville
    BillNeville
  • Derrick_Ratliff
    Derrick_Ratliff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2873 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Creating an Extended Trend Log for b3 (Infinet i1/i2) Point and Value Logs

Picard Product_Support
‎2018-09-06 10:34 AM

Last Updated: Dave_Shore Schneider Alumni (Retired) ‎2023-03-09 05:40 AM

Issue

Creating an Extended Trend Log for b3 (Infinet i1/i2) Point and Value Logs

Product Line

EcoStruxure Building Operation

Environment

  • b3 BACnet Controller
  • Infinet i1 & i2 Controller
  • Building Operation Automation Server, AS, ASP, ASB
  • Extended Trend Logs (ETLs)

Cause

Using an extended trend log to store log records for long periods of time. The extended trend log is often saved on a higher-level server with more storage capacity. This extra storage capacity enables the server to store more records before overwriting the old ones. For more information, see WebHelp. Configure extended trend logs for b3/i1/i2 devices the same way as configuring extended trend logs in other Building Operation devices. There is one difference, however. do not use smart logs when configuring extended trend logs in b3 BACnet devices. Instead of using smart logs, use the Maximum Transfer Interval property to specify the transfer interval.

Resolution

  1. In Listview, select the b3/Infinet Object (point or value), click Properties/Advanced
  2. Multiply the "Log records" by the "Log interval" to calculate the maximum transfer interval.
    The "maximum transfer interval" is the frequency at which the extended trend log will transfer log records from the b3/Infinet Object before any entries in the b3/Infinet controller log are overwritten
  3. Right click the object, choose New then "Extended Trend Log"
  4. In the Create Object box, set Smart Log to False, Set the "Maximum transfer interval" to less than that calculated above (2)
  5. Click Create

For Infinet systems always refer to Infinet under the hood otherwise the creation is as the Webhelp for creating BACnet B3 Logs
In theory it would be possible to create the Extended Trend Log in an ES (where there is more storage capacity), but this could introduce other timing and bandwidth issues, so it is usually best to keep the first Extended Trend Log in the AS, then extend this to a second Extended Trend Log in the ES, as shown. (the second ETL in the ES scan use smart logging in the usual way)

2023-03-09_13-38-41.jpg

If significant logging is required then External Log Storage should be considered. (the B3 or i1/i2 logs still need to be collected via Extended Trend Logs)

 

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • 12802
  • DavidShore19
  • DavidShore21
  • DavidShore23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore