Creating a controller offline report
  • Creating a controller offline report
  • RandyDavis
    RandyDavis
  • JonGreen
    JonGreen
Commander JonGreen Commander
‎2020-08-10 05:58 AM
on ‎2020-08-10 05:58 AM
Need to see when controllers go offline and then return online to understand how long a controller was offline.
Security Expert
Security Expert Server
Need to show IT when the controllers go down and for how long.
    1. Create a new Event Filter
      1. Events > Event Filter
    3. Name it Controller Offline/Online and click save
    4. Event Types tab, uncheck Include All Event Types
    5. Click Add and type "Controller <controller_name> offline (event server)" in the search bar that pops up
    6. Click OK
    7. Click Add again and type "Controller <controller_name> online (event server)" in the search bar
    9. Save
    10. Go to the Reports tab > Setup > Event
    11. Click the Add button
    12. Name it Controller Offline/Online
      1. under Event Filters, delete all events and click add
      2. in the Event Filters pop-up, select Controller Offline/Online from the drop-down and check "Access All Record Groups"
      3. Click OK and Save
      4. Go to the Reports Tab > Event
      5. Change the Event Report to Controller Offline/Online and execute
  • EcoStruxure Security Expert
  • JonGreen20
100% helpful (1/1)