Creating TAC Vista multi-server network

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Creating TAC Vista multi-server network
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
  • Anonymous user
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1996 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Creating TAC Vista multi-server network

Picard Product_Support
‎2018-09-07 03:33 AM

Issue

How to add another TAC Vista server node into an existing server in TAC Workstation.

Product Line

TAC Vista

Environment

Vista Workstation

Cause

Multi-sever Vista system is the system which has more than one Vista Server in the network. One Vista Server will be assigned as the master and the rest will be assigned as slaves. The order of setting multi-sever system is very important in order to make the system work properly.

Common mistakes are:

  • Vista servers have different versions.
  • Adding slave computers before adding the master computer.
  • Using same names of Vista servers.
  • Using dynamic IP address.
  • Vista Server object names are the same. All folders and objects found at the root level of the servers must be changed to unique names before merging the databases.

Resolution

Before doing that, please back up all TAV Vista databases on all computers. All computers should run the same version of TAC Vista. Also make sure all your IP networks are functioning.

In addition, all Vista Servers need to be the same version. (eg. Vista 5.1.3 server will not be able to communicate Vista 5.1.4 server when they are noded together.)

  1. All computers’ TAC Vista Servers need to have different names. The server name can be checked by opening your TAC Vista Server. By default, Server name is the computer name.
    If the sever name needs to be changed, please following the steps listed below:
    1. Go to TAC Vista Server Setup
    2. Go to Vista Database tab
    3. Under “Rename Vista Server to” text field, type the new name
    4. Click ok and start the Vista Server to make sure the name has been changed
  2. Choose one computer to be the Master and the rest of the computers will be Slaves.
  3. Start by shutting down all instances of TAC Vista Sever and TAC Vista Workstations.
  4. Add Slave Servers into the Master Server.
    1. Start the Master TAC Vista Sever, and then start its TAC Vista Workstation.
    2. Right click on the Vista Server object.
    3. Select New>Object>Node.
    4. Type $LAN.SlaveServerName.
    5. If the Slave Server name is different from its computer name, change the IP/DNS address in the property window. (Note: this step requires a static IP address)
      1. Right click on the Slave Server Node and select Properties.
      2. Type in the IP address in the IP address/DNS name field.
    6. Repeat steps a-e for any additional Slave Servers.
  5. Leave the Master Server on, and start the Slave Server.
  6. Follow steps 4 a-e for adding Master Server into Slave Server but use the Master Server’s server name and IP address this time.
  7. Then, right click on the TAC Server object in Slave Server computer, select Properties. Under the General tab, change the Network Master to the Master Server name. Then click OK.
  8. If you have multiple Slave Servers, add the Master Server into each of them.
  9. Shut down all instances of TAC Vista Workstation and TAC Vista Server.
  10. Restart the Master Server’s TAC Vista Server and its TAC Workstation first. Then start the Slave Servers’ TAC Vista Server and their TAC Workstation. You should be able to view the Slave Servers under Master Server.

Note: Master Server can view all Slave Servers’ projects, and each Slave Server can view Master Server’s project. However, each Slave Server cannot see other Slave Servers unless you node Slave Servers to each other. Any change made in Slave Server’s TAC Workstation will be reflected in the Master Server’s TAC Workstation. Vice versa also works.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4055
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore