Converting 0 - 20 mA into a 0 - 10 Volt DC signal.
  • Converting 0 - 20 mA into a 0 - 10 Volt DC signal.
  • sesa125819
    sesa125819
‎2018-09-07 06:48 AM
 To convert a 0 - 20 mA signal into an acceptable form to be used into a variety of controller types.
Sigma
BAS
Micronet
X96 controllers
X32 controllers
IAC controllers
Micronet controllers
Some controllers will not accept a 0 - 20 mA signals and therefore the signal must be converted.
To achieve this conversion, please follow the instructions below.
  1. Install a 500 ohm 0.1% resistor in series with the 0 - 20mA signal.
  2. From across the resistor, take the signal to the controller .
  3. The Universal Input or Analogue Input should be set as a standard voltage input.
Labels (2)