Controller and graphic names in Vista Workstation are red, italicized.
  • Controller and graphic names in Vista Workstation are red, italicized.
  • Ramaaly
    Ramaaly
‎2018-09-06 02:25 PM
Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-04-03 08:37 AM
TAC Vista
Vista Workstation
A red, italicized controller or graphic name indicates that this Vista object has been "checked out."  During a partial Vista database export, there is an option for whether or not to indicate the item has been checked out.  This can be used if multiple people are working on a single server from several engineering locations to prevent overlap.
To restore the database:
  1. Import the original export .zip file.
  2. If you do not have this file, you can also right click on what you want to return to normal and select "Undo Check Out."
Tags (3)