Continuum object editor crashes when applying changes to a BACnet object in a third party device.
  • Continuum object editor crashes when applying changes to a BACnet object in a third party device.
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 01:04 PM
When changes are made to the BACnet schedule in a third party device, the object editor crashes when the changes are applied.
ACCTrace file shows the following error:
The datatype of a BACnet property value specified in a service parameter does not match the datatype of the property referenced by the specified Property_Identifier.
CyberStation
Continuum
BACnet
Trane SC Schedule Object
The object type is not fully support by the third party controller.   Consult the devices PICS statement.
In some cases third party vendors will implement BACnet object types for internal use while not allowing other vendors to write to these object.
Occasionally it may be possible to write values to some of the objects properties.  However, when Continuum tries to write to a value to the unsupported property the object error will crash.
  • 6604