Continuum controller CPU light solid or not illuminated.
  • Continuum controller CPU light solid or not illuminated.
  • Dave_Shore
    Dave_Shore
  • DavidChild
    DavidChild
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 10:50 AM
Last Updated: Sisko DavidChild Sisko ‎2022-01-06 06:16 AM
  • Controller is unresponsive and does not respond to a hard reset or power cycle with the battery disconnected..
  • CPU light remains on constantly.
Andover Continuum
  • InfinityController, b3 Controller
  • NetController II, CX9680
  • ACX57
  • bCX
Controller stopped functioning after power cycled.
  • Test controller with a known working PS power supply and/or test the supply voltage is correct
  • If the controller still does not respond to a hard reset then return for repair. See the appropriate manual for reset instructions