Continuum SQL database marked as 'Suspect'

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Continuum SQL database marked as 'Suspect'
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Clifton_eakes
    Clifton_eakes
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2095 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Continuum SQL database marked as 'Suspect'

Picard Product_Support
‎2018-09-06 12:22 PM

Last Updated: Picard RobertAndriolo Picard ‎2022-03-11 02:21 PM

Issue

CyberStation is unable to connect to the database.

ODBC test also fails when testing the connection to the database.

Product Line

Andover Continuum

Environment

  • CyberStation
  • SQL server
  • SQL management studio

Cause

SQL server not on UPS.

Server shut down due to a power failure.

Looking at the ContinuumDB using the SQL Management Studio shows the database has been marked as suspect.  ContinuumDB (SUSPECT)

The database may be marked suspect for the following reasons

  • System Issues
  • Transaction Log File is Missing
  • SQL Server Crash
  • Database Files are inaccessible
  • SQL Server Database Operation Failures
  • Due to Improper shut down of SQL Server System (as mentioned above)
  • Due to Sudden Power Outage
  • Low Disk Space Issues
  • Hardware Failure

Resolution

The database may have been damaged by the ungracious shutdown.

The restore option is grayed out and must first be re-enabled before a restore operation can be allowed.

How to recover a database in suspect mode

  1. Clear the suspect mode of the database using sp_resetstatus DatabaseName. This will clear the suspect flag and make the database available online. The SQL Server must be stopped and re-started.
  2. Change the database status to Emergency using the following command.
    ALTER DATABASE DatabaseName SET EMERGENCY;
  3. Restrict database to single user by changing the access mode as mentioned below
    ALTER DATABASE DatabaseName SET SINGLE_USER;
    If the restore option is now enabled skip step 4
  4. Run the CHECKDB command with “REPAIR_ALLOW_DATA_LOSS” option. This option should be tried as the last option as it always behaves the way it is named. We are not sure of what data it removes.
    DBCC CHECKDB (DatabaseName, REPAIR_ALLOW_DATA_LOSS) WITH NO_INFOMSGS, ALL_ERRORMSGS
    If the repair operation is successful the database is now usable but if a recent backup is available it is strongly recommended to restore the database.
  5. Restore the most recent backup of the Continuum database.
  6. Set the ContinuumDB owner using the query
    SP_ChangeDBOwner 'Andover97'

 

Labels (1)
Labels:
  • Andover Continuum
Tags (3)
  • Find more articles tagged with:
  • 7899
  • CliftonEakes22
  • RobertAndriolo22
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore