Continuum Database Sizing and SQL Server selection

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Continuum Database Sizing and SQL Server selection
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3011 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Continuum Database Sizing and SQL Server selection

Picard Product_Support
‎2018-09-07 05:20 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:08 AM

Issue

How do you determine how large a database will grow when using Continuum? How do you know if a Stand Alone or LAN install should be used? Which version of Microsoft SQL Server is needed?

Product Line

Andover Continuum

Environment

  • Windows XP
  • Windows Vista
  • Windows Server 2003
  • Windows Server 2008
  • MSDE
  • SQL Express
  • SQL Server Standard
  • SQL Server Enterprise

Cause

A database will grow based on the number of objects and logging requirements for a project. Estimating how much a database will grow over time based on the number of controllers, points and logging should be done to determine which Microsoft Database solution is needed for the site.

Microsoft has placed database size limitations on the free versions of their database engines called MSDE and SQL Server Express. The size limitations are 2 and 4 gigabytes respectively. If this size limitation is exceeded, it can produce unwanted results including database corruption. If the estimated size of a database over time exceeds these limitations then a full Microsoft SQL version must be implemented.

Resolution

An Excel spreadsheet has been developed to help evaluate the size of a Continuum database, to determine if a Stand Alone or LAN is needed and which version of SQL should be used. The Continuum database estimating spreadsheet takes into consideration 6 main areas:

  1. Extended Logs- total amount of logs, intervals and the number of days to retain 
  2. Access Events- total amount of access events and the number of days to retain
  3. Alarm Events- total number of alarms and the number of days to retain
  4. Error Events- total number of Cyberstation errors and the number of days to retain
  5. Activity Events- total number of Activity events of all Continuum users and the number of days to retain
  6. Continuum Database objects- Total number of Netcontrollers, Infinet, BCXs , mstp controllers, total number of inputs, outputs and numerics. Any of the objects not mentioned above.
Consider all objects not mentioned above

The number of data logs, extended log intervals, number of days to retain data and other estimation information can be inserted into the spreadsheet. The sheet will calculate the information and do the following:

  1. Estimate the space required for that object type and the sum of all object types
  2. Indicate if a Stand Alone or LAN system is needed
  3. Indicate which version of SQL Server is needed

Download the Continuum Database Size Estimation Tool.

Labels (1)
Labels:
  • Andover Continuum
Attachments
Tags (1)
  • Find more articles tagged with:
  • 4460
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore