After installing Continuum 2.0 SP1 problems are found with two of the System Default Listviewis.
  • Errors This Month returns no results.
  • Personnel_Expired Cards shows all cards not just expired cards.
  • Continuum 2.0 SP1
  • Cyberstation
  • ListViews
  • Filters
Misconfigured Listview qualifier or filter.
Errors This Month
The filter in the listview configuration is set to Root\OneMonthToNow.  It should be set to Root\MonthToNow.
The listview qualifier needs to be configured as shown below.