Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Connection Objects in Xenta Server effect on I/NET system

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Connection Objects in Xenta Server effect on I/NET system
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • SESA116857
    SESA116857
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1738 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Connection Objects in Xenta Server effect on I/NET system

Picard Product_Support
‎2018-09-06 01:23 PM

Issue

What are the effects of a connection object on the I/NET controller lan?

Product Line

Satchwell MicroNet, TAC INET, TAC Vista

Environment

Xenta 527/913/731

I/NET

Cause

The I/NET communication protocol has a maximum baud rate of 19,200 bps and this allows for a maximum of 10 messages a second to occur on the I/NET controller lan. This limit applies to the entire controller lan not just a single controller.

Optimal performance will be at 5 or 6 messages a second on the controller lan.

Resolution

Any connection objects involving I/NET points need to be aware of the limits imposed by the controller lan protocol and adjust the periods of connection objects to avoid exceeding these limits.

Every connection object that the source is from I/NET requires the value to be read from the I/NET controller before it can determine if the value has changed to send to the target of the connection object. If the default period of 10 seconds is used for all connection objects then only 100 points will consume 100% of the bandwidth on the I/NET controller lan to meet the demand and negatively impact the performance of the I/NET network.

Instead count the number of connection objects with source values from I/NET. Divide this number of 4 to allow room for values being written to the I/NET network to determine the minimum recommended period for your connection objects to avoid overloading your I/NET controller lan.

Ex: 250 points being sent from I/NET to a 3rd party system / 4 writes a second = 63 second period.

This could result in some larger then expected periods and some points might be more critical then others which will require some prioritization. If of the 250 points only 15 require faster response time then they can use a lower period, but this will affect the period used for the lower priority points. It is recommended to avoid periods below 10 seconds if at all possible.

Ex: 235 points at lower priority / 4 messages a second = 59 second period

59 second period for low priority points / 10 second period of high priority points = 6 polls per point * 15 points at high priority = 90 reads for high priority points.

235 points + 90 polls = 325 values read from I/NET / 4 messages a second = 82 second period for lower priority points to accommodate 15 high priority points.

Labels (3)
Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 6013
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore