Issue
Multiple passive 4-20mA sensors require an external power supply when connecting to a Sigma controller.
How can this be done correctly and safely?
Product Line
Satchwell BAS & SigmaEnvironment
- Sigma UNC Controller
- Passive 4-20mA Sensors
- External Power Supply (12V DC or 24V DC)
Cause
Unlike active 4-20mA sensors, which include an internal power source, passive sensors do not.
Therefore, an external power supply is necessary to operate them when interfacing with a Sigma controller.
Resolution
To connect multiple passive 4-20mA sensors to a Sigma controller:
-
Use a dedicated external power supply for each sensor.
- Voltage: 12V DC or 24V DC, depending on sensor specifications.
-
Wiring Instructions:
- Connect the positive terminal of the power supply to the positive input of the Sigma controller.
- Connect the negative terminal of the sensor to the common ground.
-
Configure Sigma Controller:
- Ensure the Universal Input jumper settings are correctly set to current (mA) mode.
- Verify input scaling and calibration in the Sigma software to match the sensor's output range.
-
Best Practices:
- Use shielded cables to minimize electrical noise.
- Label each sensor connection clearly for maintenance and troubleshooting.
- Avoid sharing power supplies between sensors unless specifically supported by the sensor manufacturer.
- Always consult the sensor's datasheet for exact wiring and voltage requirements.