Issue
Product Line
TAC IA SeriesEnvironment
- Niagara R2 system
- LPR-10
Cause
Resolution
Follow these steps to configure the LON Router:
-
Prepare the Network:
- Cut the existing LonRouter and Channel1 from the station.
- Set the status of all Lon devices to Unknown.
-
Define Router and Channels:
- Refer to the procedure starting on page A-9 of the Niagara LonWorks Integration Guide.
- Define the LonWorks network, router, and associated channels before running any automated processes.
-
Install Termination Devices:
- Ensure four LON-TERM-2 devices (LON BUS Topology Terminators) are installed:
- One at each end of the trunk.
- One at the near end of the router.
- One at the far end of the router.
- Ensure four LON-TERM-2 devices (LON BUS Topology Terminators) are installed:
-
Verify Configuration:
- After defining the router and channels, proceed with LonDeviceManager operations.
- Confirm device statuses and communication integrity.