Issue
How to configure a G3 station as a BACnet BBMD
Product Line
TAC IA SeriesEnvironment
I/A Series G3 version 3.3.22 and later
Cause
Documentation
Resolution
- In the G3 Station, expand the BacnetNetwork, expand Bacnet Comm, expand Network, and then double-click IP Port. The IP Port Property Sheet opens (see below)
- In the IP Device Type drop-down, select Bbmd. Click Save
- The station is now configured as a BACnet BBMD