Issue
Can Cyberstation setup and configure 3rd party BACnet devices.
Product Line
TAC IA Series, Andover Continuum
Environment
- Cyberstation BACnet
- I/A Series MNB-1000
Cause
It is desirable to configure all products from the same software.
Resolution
Cyberstation and the BACnet protocol do not allow you to do basic setup and configuration of 3rd party devices, most products will have their own configuration software or local display/ keypads for setup.
The I/A MNB-1000 BACnet controllers will require I/A Series Software to setup and configure the controllers, this can not be done through Cyberstation.
Once setup and communicating Cyberstation will be able to make changes / adjustments depending upon the PIC's statement of the device.