Configuring Daylight Savings Time in I/NET

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configuring Daylight Savings Time in I/NET
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Tom_Poovey
    Tom_Poovey
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2313 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuring Daylight Savings Time in I/NET

Picard Product_Support
‎2018-09-07 09:07 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-10-06 10:23 AM

Issue

Configuring Daylight Savings Time. What is the proper way to do this?

Product Line

TAC INET

Environment

I/NET

Cause

There are two different ways to setup the Daylight Saving Time in I/NET.

Daylight Saving Time DST is not observed in Queensland, the Northern Territory or Western Australia, South Africa, and other parts of the world. The document below shows how to set 0 in the DST settings.

If using a revision of I/NET prior to 2.21 be reminded that the DCU time sync problem in the ReadmeSeven.txt is not just pertaining to the error generated by not having DST settings for the controller. 2.21 is referring to the version where this was fixed. Also note that when upgrading a site, go all the way to 2.31 at least because it solved problems which were in the previous revisions.

Resolution

Option #1: Using Windows time and NO controller time synch

  1. Set Windows Time for daylight savings changes. Remember to change the time zone for you location. In my example I am in the Central time zone.
    datetimeproperties.png
  2. Set the Inet Host settings to do Time Sync. Function for all the controllers you wish to time sync with the PC.
    networkfunction.png
  3. Enable the Daylight Savings settings using the "Setup" button.
    dstsynch.png
  4. This is the correct settings for the controller configuration. Note if you set the daylight settings in this format you will get a 2 hour shift up or back. The daylight setting must be set to zero (0)
    dcuconfig.png

 

Option #2 Using Windows time and controller time synch

  1. Set Windows Time for daylight savings changes
    timezone.png
  2. Set the Inet Host settings to NO Time Sync. Function
    dcusynch.png
  3. This the correct setting for this controller configuration using the controller to shift the daylight saving time
    dcuconfig2.png

 

The Daylight Savings times were set by the Congress of the USA in 2004

The beginning was to be the second week of March on a Sunday.

This comes out in I/NET as being

  • Month = 3
  • Week = 2
  • Day = 1 (Sunday is always day 1 Thus Saturday is day 7)

The ending was to be the first week of November on a Sunday

This comes out in I/NET as being

  • Month = 11
  • Week = 1
  • Day = 1 (Sunday is always day 1 Thus Saturday is day 7)

globaltimezone.png

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 1752
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore