Configuration of multiple BACnet BBMD's over several subnets

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configuration of multiple BACnet BBMD's over several subnets
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support
  • Carl_Slack
    Carl_Slack
  • DavidChild
    DavidChild

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
7275 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuration of multiple BACnet BBMD's over several subnets

Picard Product_Support
‎2018-09-07 03:05 AM

Last Updated: Administrator CraigEl Administrator ‎2022-09-12 09:25 PM

Issue

Configuration of multiple BACnet BBMD's over several subnets

Product Line

Andover Continuum, EcoStruxure Building Operation

Environment

Bacnet BBMD

Cause

Bacnet Broadcast communication through IP router

Resolution

Configuration of multiple BBMD's over several subnets:

bacnet-udpip-subnet-illustration.png

INCORRECT METHOD

For example if there are 4 subnets on the same B/IP (BACnet IP Network):

  • Subnet 1: Workstation setup as a BBMD with an entry in the Broadcast Distribution Table for each BCX
  • Subnet 2: BCX setup as a BBMD with an entry in the Broadcast Distribution Table for itself and the Workstations BBMD Only.
  • Subnet 3: BCX setup as a BBMD with an entry in the Broadcast Distribution Table for itself and the Workstations BBMD Only.
  • Subnet 4: BCX setup as a BBMD with an entry in the Broadcast Distribution Table for itself and the Workstations BBMD Only.

The BCX's do not reference any points from each other. Since there is no data sharing between the BBMD's, one might think that in each BCX's Broadcast Distribution Table that there would only be a need to add one entry for the Workstations BBMD. Sounds like with this setup we'll reduce traffic by only adding the one entry in each BCX's BBMD Broadcast Distribution Table.

The above scenario could in fact slow down a network and cause unnecessary traffic.

 

The supported method is that every BBMD on a B/IP network have the same routing tables(better known as the Broadcast Distribution Table) as in the below configuration.

CORRECT METHOD

For example there are 4 subnets on the same B/IP (BACnet IP Network).

  • Subnet 1: WS BBMD with an entry in the Broadcast Distribution Table for itself and all BCX's setup as BBMD on the same B/IP.
  • Subnet 2: BBMD with an entry for all BBMD's(including self) in the Broadcast Distribution Table on the same B/IP.
  • Subnet 3: BBMD with an entry for all BBMD's(including self) in the Broadcast Distribution Table on the same B/IP.
  • Subnet 4: BBMD with an entry for all BBMD's(including self) in the Broadcast Distribution Table on the same B/IP.

The entry below can be found in the BACnet Standards 2004:

 

J.4.3 BBMD Concept

Each IP subnet that is part of a B/IP network comprised of two or more subnets shall have one, and only one, BBMD. Each BBMD shall possess a table called a Broadcast Distribution Table (BDT) which shall be the same in every BBMD in a given B/IP network.

Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 3064
  • CraigEllis22
  • DavidChild20
Was this article helpful? Yes No
75% helpful (3/4)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore