Completely removing the obsolete TrendLog objects from the EBO servers and the Extended Log Storage (PostgreSQL/TimescaleDB) database.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Completely removing the obsolete TrendLog objects from the EBO servers and the Extended Log Storage (PostgreSQL/TimescaleDB) ...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2005 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Completely removing the obsolete TrendLog objects from the EBO servers and the Extended Log Storage (PostgreSQL/TimescaleDB) database.

Lieutenant | EcoXpert Master SangKim Lieutenant | EcoXpert Master
‎2022-08-23 10:07 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:33 AM

Issue

When EBO servers (ES & AS) no more need to keep the unnecessary TrendLog objects, the obsolete objects need to be deleted from EBO servers, and their log data need to be removed from the Extended Log Storage (PostgreSQL/TimescaleDB) server as well. 

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Automation Server
  • External Log Storage
  • PostgreSQL (pgAdmin 4)
  • TimescaleDB 

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

Deleting the obsolete TrendLog objects from EBO servers does not remove the old log data of the obsolete TrendLogs left in the PostgreSQL/TimescaleDB database.

Resolution

Once the obsolete TrendLog objects are deleted from EBO servers, their log data are no longer saved in the PostgreSQL/TimescaleDB. The next task is removing the old log data left in the PostgreSQL/TimescaleDB database.

 

1. As always, backup current EB & AS’s databases from EBO workstation.

 

2. As always, backup the current PostgreSQL/TimescaleDB database and save to a safe location.

  1. Backup the “ebo_db” from the PostgreSQL/TimescaleDB server using the pgAdmin 4 (refer to https://www.pgadmin.org/docs/pgadmin4/development/backup_dialog.html , or refer to page 8 “Backup” section of the “EBO External Log Storage Installer.pdf” document for detail).

 3.Remove the obsolete TrendLog from the PostgreSQL/TimescaleDB database (the “ebo_db”).

  1. Method_1: Delete the EBO TrendLog object from ES & AS’s & TimescaleDB using EBO workstation.

(1) From the EBO workstation, expand the folder (location) of the TrendLog object, and delete the TrendLog object.

(2) From the EBO workstation, go to the TimescaleDB folder (/Server 1/System/External Log Storage/TimescaleDB/Trend /Logs/Tree View), and delete the Trendlog object from PostgreSQL/TimescaleDB database.

(3) Verify the TrendLog disappears from both the EBO and the PostgreSQL/Timescale DB.

 

  1. Method_2: If the above Method1 takes a long time to complete, you can delete the TrendLog objects from PostgreSQL/TimescaleDB database directly. 

(1) From the EBO workstation, expand the folder (location) of the TrendLog object, and delete the TrendLog object. (Same as item (1) of the above Method_1)

(2) From the PostgreSQL/TimescaleDB server, run the pgAdmin 4, select the “ebo_db”, open the “Query Tool”, and execute the below scripts:

Find the ID of the obsolete TrendLog from the trend_meta table.

Select Externallogid, source from trend_meta where sources like '%TrendLog Name or Path%'

Remove the TrendLog from the 2 tables using the above found Externallogid as below.

Delete from trend_data where externallogid = 1234567890

Delete from trend_meta where externallogid = 1234567890

(3) Verify the TrendLog disappears from both the EBO and the PostgreSQL/Timescale DB.

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • SangKim22
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore