Commissioning IO modules knocks NetController II offline.
  • Commissioning IO modules knocks NetController II offline.
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 12:23 PM
Each time an I/O module is commissioned the NetController II goes offline.
  • IO modules
  • NetControllerII
  • CX9680
If there is a problem with the controller configuration it may be possible to commission the IO modules on an empty controller.
The controllers would then have to be reloaded by class or may have to be rebuilt manually.
  1. Access the controllers webpage.
  2. Select Clear Database Backup
  3. Commit changes to the controller.
  4. Do not reload the controller.
  5. Commission the IO modules on the empty controller.
  • 7877