Issue
At time it is necessary when troubleshooting to check specific communication settings on a comm port
Product Line
Andover Continuum
Environment
- Continuum
- Windows XP
- Windows Vista
- Windows 7
- Windows Server 2003
- Windows Server 2008
Cause
Specific commands needed to check communication parameters with precision and to edit them if necessary
Resolution
Examples of command line parameters needed for Xdriver modbus communication.
| Command | Result |
| p comm2 defaultbaud | 9600 |
| comm2 defaultbaud=baud19200 | (To set) |
| p comm2 defaultbaud | 19200 |
| p comm2 parity | None |
| comm2 parity=Odd | (To set) |
| p comm2 parity | Odd |
| p comm2 stopbits | stopbits1 |
| comm2 stopbits=stopbits2 | (To set) |
| p comm2 stopbits | stopbits2 |
| p comm2 datalength | databits8 |
| comm2 databits=databits7 | (To set) |
| p comm2 datalength | databits7 |