Cisco switches reporting connected Sigma devices using more than one MAC Address.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Cisco switches reporting connected Sigma devices using more than one MAC Address.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1216 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Cisco switches reporting connected Sigma devices using more than one MAC Address.

Picard Product_Support
‎2018-09-07 01:26 PM

Issue

Cisco switches reporting connected Sigma devices using more than one MAC Address which appear to be transmitted from the Sigma device connected to the port. 

The error alarm reported "%PORT_SECURITY-2-PSECURE_VIOLATION: Security violation occurred, caused by MAC address 0050.b401.1e46 on port FastEthernet1/0/35"

Environment

All ARM7 Sigma Ethernet devices

  • Cisco Catalyst 3550 Series Switches
  • Cisco Catalyst 3560 Series Switches
  • Cisco Catalyst 3560-E Series Switches
  • Cisco Catalyst 3750-E Series Switches

     

Cause

  1. Sigma controllers broadcasting high number of Sigma globals (typically 40 per second). Upgrading BAS2800+ systems to Sigma can result in higher levels of Sigma global data than seen previously.
  2. Cisco switch set to 10Mb half duplex which mistakes the source MAC address of the Sigma global from a controller on one port with that of a controller on another port.
  3. Cisco switch has Layer 2 Security feature enabled, see Click Here
  4. High collision rates may also be seen at the switch.

Resolution

  1. Identify those Sigma objects that are broadcasting global data at high rates and suppress the rate of change of the Sigma object.
    This can be achieved by:
    1. Running Wire Shark Ethernet trace program to record the Sigma broadcast Ethernet packs per Ethernet sub-LAN.
    2. Email each of the saved capture files (per LAN) to your local product support for a global analysis report.
  2. If possible then increase the connection speed of the Cisco ports.
  3. New firmware for the ARM processors has been created to addresses the issue. You can find the firmware and release note on the Exchange
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (1)
  • Find more articles tagged with:
  • 4748
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of