Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Cisco Switches Reporting Sigma Devices with Multiple MAC Addresses

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Cisco Switches Reporting Sigma Devices with Multiple MAC Addresses
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1467 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Cisco Switches Reporting Sigma Devices with Multiple MAC Addresses

Picard Product_Support
‎2018-09-07 01:26 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-08 11:43 PM

Issue

Cisco switches are reporting connected Sigma devices using more than one MAC address. This results in error alarms such as:

%PORT_SECURITY-2-PSECURE_VIOLATION: Security violation occurred, caused by MAC address 0050.b401.1e46 on port FastEthernet1/0/35

Product Line

Satchwell BAS & Sigma

Environment

All ARM7 Sigma Ethernet devices

  • Cisco Catalyst 3550 Series Switches
  • Cisco Catalyst 3560 Series Switches
  • Cisco Catalyst 3560-E Series Switches
  • Cisco Catalyst 3750-E Series Switches

Cause

 

  • Sigma controllers are broadcasting a high volume of Sigma global data (typically ~40 broadcasts/sec).
  • Upgrading BAS2800+ systems to Sigma increases the volume of global data.
  • Cisco switches set to 10Mb half duplex may misinterpret the source MAC address of Sigma globals, causing cross-port MAC confusion.
  • Layer 2 Security features on Cisco switches may trigger violations.
  • High collision rates may also be observed on affected switch ports.

Resolution

  1. Identify High-Rate Sigma Objects:

    • Use Wireshark to trace Ethernet traffic and identify Sigma objects broadcasting at high rates.
    • Capture traffic per Ethernet sub-LAN.
  2. Submit for Analysis:

    • Email the capture files to your local product support team for a global analysis report.
  3. Optimize Network Configuration:

    • If feasible, increase the port connection speed on Cisco switches.
    • Avoid using 10Mb half duplex settings.
  4. Firmware Update:

    • New firmware for ARM processors has been released to address this issue.
    • Refer to the Exchange for firmware and release notes.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 4748
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore