Check Xenta programmable online status from a Xenta 5/7/9xx LON node

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Check Xenta programmable online status from a Xenta 5/7/9xx LON node
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2389 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Check Xenta programmable online status from a Xenta 5/7/9xx LON node

Picard Product_Support
‎2018-09-06 01:48 PM

Issue

A Xenta 5/7/9xx controller can either be implemented as

  • A Xenta Server, where it doubles as the LonTalk adapter and a Xenta device
  • A LON node, where it is a part of an LNS database below a different LonTalk adapter

If the Xenta is a LON node, then it will be represented as a LON device in the network, but also utilizes Xenta Group Bindings to communicate to Xenta programmable controllers (280/300/401). If graphic pages in certain Xenta units aren't displaying data, or connection objects aren't passing data as expected, the online status of the Xenta units should be checked not from the Vista Server, but from inside the Xenta 5/7/9xx. This issue will display red x's on the graphics page.

Product Line

TAC Vista

Environment

  • Xenta 511, 527, 701, 711, 721, 731, 913
  • LNS Database

Cause

A Xenta 5/7/9xx LON node pulls "double duty" as both a LON device and a Xenta Lacnet device. It requires one Xenta Group Binding on message tag 0 to facilitate communication with Xenta programmable controllers.

Resolution

  1. Log into the web interface for the 5/7/9xx.
  2. Navigate to Utilities > LacNet > LacNet List Xenta.  "LacNet" refers to proprietary Xenta communication.
  3. View the online status of each Xenta programmable controller in the network.  It is displayed as below:

    ===============================================
    Node: RTU7
    Xenta group: XG_RTUS  GroupMaster:No
    FTP state alarmstack, app:finished OnOff:N/A
    Latest FTP : 05/13/2011 11:25:59

    State: online (since 05/13/2011 11:23:05)
    Xenta???  Software version: 3.84-01
    NID: 04:6B:84:9F:01:00  Subnet/Node:  253/122


    Module: SUMMARY
    Module: CALIBRATE
    Module: CONFIGURE
    Module: ALARMS
    Module: SETPOINTS
    Module: ERRORS
    Module: $LOG
    Module: $SYSTEM
    Module: $SYS
    Number of alarm objects: 25
    Number of public signals: 7
    Number of handles allocated: 8, where 1 is with notification


    ===============================================

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5221
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.