Changing a Doors Door Type based on Arm State of the Area

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Changing a Doors Door Type based on Arm State of the Area
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AdamSteele
    AdamSteele
  • BillNeville
    BillNeville

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1325 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Changing a Doors Door Type based on Arm State of the Area

Captain BillNeville Captain
‎2021-09-01 01:53 AM

Last Updated: Guinan AdamSteele Guinan ‎2021-09-09 02:21 AM

Issue

This is useful when you are disarming areas from a card reader as you can secure the disarming portion by requiring a PIN code, preventing somebody from using a lost or stolen card to disarm the area while maintaining the convenience of Card Only once disarming has occurred.

Product Line

Security Expert

Environment

  • Security Expert Client
  • Security Expert Server
  • SP-C-Web

Cause

Prevent someone from using a lost or stolen card to disarm an area while maintaining the convenience of Card Only once disarming has occurred.

Resolution

  1. Create a new Schedule (SX = Sites > Schedules, SPC-Web = Time > Schedules) with the following settings:
    1. Check/enable all days for Period 1, leave start and end times default so you are left with a 24/7 schedule
    2. Under Options enable 'Validate Schedule When Qualify Output is On', set the 'Qualify Output' to whatever output is configured as the Disarmed output for the required Area.
    3. If you aren’t using a disarmed output currently you will need to assign one, this can be a Virtual Output if you do not want to use a physical output.
  2. Create a new Door Type (Programming > Door Types) with the following settings:
    1. Operating Schedule = The schedule from Step 1
    2. Secondary Door Type = The default Card AND PIN door type created by the system
    3. Entry Reading Mode = Card Only
    4. Exit Reading Mode = Card Only
  3. Locate the required Door(s) (Programming > Doors) and change the Door Type to the one created in Step 2.

When the Area is disarmed the schedule will be valid so the Door Type will be Card only when the schedule is invalid (which will be whenever the area is armed as the disarmed output deactivates upon arming) the secondary door type of Card + PIN will be used.

You can use other combinations of Door Types as required

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • BillNeville21
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore