Changing a Controlli MVL56C actuator with an SE Forta actuator when fitted to an VMB16 - 125 Controlli valve.
  • Changing a Controlli MVL56C actuator with an SE Forta actuator when fitted to an VMB16 - 125 Controlli valve.
  • sesa139513
    sesa139513
  • sesa125819
    sesa125819
‎2018-09-06 09:48 AM
Changing a Controlli MVL56C actuator.
MVL56C
VMB
VMB16
A Controlli MVL56C actuator is to be replaced, is a linkage required to connect to a Forta actuator?
A linkage is required.
The linkage is the AG50, part number 880-0127-000
  • Field Devices
  • 15227