Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Changing Format attribute of AnalogInput gives an error "An attempt has been made to write a property defined as inaccessible through the BACnet protocol write services"

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Changing Format attribute of AnalogInput gives an error "An attempt has been made to write a property defined as inaccessible...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • PaulFr
    PaulFr
  • DavidChild
    DavidChild
  • YangboLIU
    YangboLIU
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1943 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Changing Format attribute of AnalogInput gives an error "An attempt has been made to write a property defined as inaccessible through the BACnet protocol write services"

Product_Support
‎2020-09-21 06:13 AM

Last Updated: CraigEl Champion ‎2020-09-21 07:02 PM

Issue

When opening a BACnet AnalogInput  from (the Blue) BACnet device side, the value of the object displays as 3 decimal digits by default. The format can be changed in the format field as desired, however when clicking the "Apply" button, an error prompt box pops up with the message "An attempt has been made to write a property defined as inaccessible through the BACnet  protocol write services". if the "Apply" buttonis clicked again, the error disappears and the format is been changed successfully.

Product Line

Andover Continuum

Environment

  • Continuum BACnet
  • BCX1
  • B3s
  • Cyberstation
  • V2.02 and earlier.

Cause

Format is not a standard BACnet property, it is a Continuum attribute and when the format is changed Cyberstation sends a command to change the "present value" of the point in the controller. The present value of AnalogInput cannot be written so the error occurs. When clicking "apply" or "OK" for the second time Cyberstation only writes the attribute of the point in the database rather than the controller. Therefore we can get a successful change of format for AnalogInput by clicking "Apply" twice.

For AnalogValue, the "present value" of  AnalogValue can be written in BACnet, so there is no error when changing the format of an AnalogValue.

Resolution

Ignore the error when making the change, click the "Apply" button twice after updating the "Format".

Or upgrade to V2.03 where this issue has been resolved.

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 11127
  • PaulFrost20
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.