Change the Door Mode (EntryNormMode) from SiteMode+CardMode to PinMode in PE program
  • Change the Door Mode (EntryNormMode) from SiteMode+CardMode to PinMode in PE program
  • SangKim
    SangKim
  • AbeMeran
    AbeMeran
‎2018-09-06 01:15 PM
Last Updated: Administrator DavidFisher Administrator ‎2019-11-05 02:25 PM
Door needs to be set to SiteMode+CardMode for weekdays and SiteMode+CardMode+PinMode for weekends.
Andover Continuum
  • NetController (CX9900 , CX9940 , CX9702 , ACCX5740 , ACX5730)
  • InfinetController (ACX780, ACX781)
Customers want to have a PE program that changes the door mode to be more secured for the weekend according the building schedule.
In the PE program ;
Set DoorName\EntryNormMode = 3  ' Set the door mode to SiteMode+CardMode for weekdays
Set DoorName\EntryNormMode = 11 ' Set the door mode to SiteMode+CardMode+PinMode for weekends.
The values for the different modes are:
  • 1 = SiteMode
  • 2 = CardMode
  • 4 = GeneralMode
  • 8 = PINMode
  • 16 = ScheduleMode
The individual values are added together to obtain the desired mode. As seen above, setting the mode to 3 makes the door validate site + card.
It is recommended that both the normal and nocomm modes be set (EntryNormMode, EntryNoCommMode)
For a dual reader door, use the corresponding ExitNormMode and ExitNoCommMode.