Change out a failed B4920 or BACnet BCX controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Change out a failed B4920 or BACnet BCX controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • ScottLeedberg
    ScottLeedberg
  • BillNeville
    BillNeville
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3303 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Change out a failed B4920 or BACnet BCX controller

Picard Product_Support
‎2018-09-06 03:01 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-06-17 02:13 PM

Issue

How do I change out a failed B4920 or BACnet BCX controller?

Product Line

Andover Continuum

Environment

  • B4920
  • BACnet BCX controller

Cause

Failed device

Resolution

  1. Place Cyberstation Offline.
  2. Edit existing B4920 or BCX Controller object on the Infinity side and note the following:
    1. ACC Net ID
    2. BACnet Device ID
    3. Network ID - UPD
    4. Network ID - Comm2 (MS/TP network ID)
    5. IP Address, Subnet Mask, Default Router (Gateway) Address
    6. Name of the controller
  3. Physically disconnect power and MS/TP data cables from existing B4 or BCX Controller.
  4. Remove existing B4 or BCX Controller.
  5. Install replacement B4 or BCX Controller.
  6. Connect MS/TP data cable to the replacement B4 or BCX Controller.
  7. Connect power to the replacement B4 or BCX Controller.
  8. Use a web browser to connect to the login page of the B4 or BCX at IP Address 169.254.1.1.
  9. Use the controller configuration web page to configure the following values:
    1. ACC Net ID (enter the value from Step 2 a)
    2. BACnet Device ID (enter the value from Step 2 b). This is very important - do not use the new controller's serial number or you will likely have trouble communicating with the new controller on the BACnet side. 
    3. BACnet Network ID - UDP (enter the value from Step 2 c)
    4. BACnet Network ID - Comm2 (enter the value from Step 2 d)
    5. IP Address, Subnet Mask, Gateway Address (enter the values from Step 2 e)
    6. Name (enter the value from Step 2 f)
    7. If this device is a BCX, the user will want to reset the BACnet MAC ID - Comm2 value, if that value was non-zero in the device being replaced (there is no record of this value in Cyberstation).
  10. Click the Submit to Controller button then Commit Changes button and then CommitChanges/Restart Controller button. Allow sufficient time for the controller to restart.
  11. In CyberStation, on the Infinity side, edit the controller object and change the serial number to that of the new controller. Save the object.  
  12. Go back to Online mode in CyberStation. The new B4 or BCX should now be online in the Infinity view.
  13. Reload the B4 or BCX Controller.
  14. Verify existing Points and Programs are running correctly.
  15. Perform a “Backup to Flash” operation on the B4 or BCX Controller.
  16. Check that the controller is online in the BACnet side. Note that the Device Node ID on the BACnet side is the serial number of the old (replaced) controller. This is as it should be since we do not want to create a new BACnet device; we just want to replace the controller hardware.
  17. Edit objects on the BACnet side to verify that there are no errors.  
  18. Test alarms, graphics, communication to b3's/3rd party devices, etc. 
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 2450
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore