Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Caution when using PE programs to perform an automatic flash backup on a controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Caution when using PE programs to perform an automatic flash backup on a controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • sesa119747
    sesa119747
  • Carl_Slack
    Carl_Slack
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1863 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Caution when using PE programs to perform an automatic flash backup on a controller

Picard Product_Support
‎2018-09-06 02:53 PM

Issue

Extreme care must be used when using PE programs to perform an automatic flash backup on a controller

Product Line

Andover Continuum

Environment

  • Infinet Controller
  • BACnet Controller

Cause

An incorrect code in the program can cause issue to the controller and require a full reload.

Resolution

BEWARE of PE programs that set the flag to flash a controller

Infinet and BACnet controllers that have the ability to have their objects backed up to flash and running a program to reflash them when the application data changes should be used with extreme caution.

If you accidently created a program that looped and continuously wrote
Accstatusbackup = accbackupnow
and tried to change the application data such as creating a point or editing a
program you will receive an error stating "OMS database not currently available (Backing Up)"
This type of program is very bad, and can reset the controller requiring a full reload.

This is not to say that such programs shouldn’t be created to reflash a controller when needed, just create them as a fall thru or stop the program at the end of execution and have them triggered ie... a certain time of the day and test to see if there needs to be a reflash ie...

If accstatusbackup = accbackupneeded then
Accstatusbackup = accbackupnow
Endif

Also keep in mind that flash memory circuits are rated for a maximum of 100,000 write operations and there is an automatic software based circuit breaker that will set the accstatusbackup to accbackupdisabled when 10,000 writes occur. This should be considered a safety net that the controller has been flashed 10,000 times, that would be a good point to ask "WHY". You can reset this by setting the accstatusbackup = accbackupenable and you’ll be able to continue to write to the flash.

It would be a good practice to have a numeric that is alarmed to notify in the event of the controller excessively writing the flash. This number could be whatever you think your threshold for writes should be ie.. if you wanted to know when the controller has been flashed > 20 you would know that something is probably happening and maybe you should address it.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 2821
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of