Cause and action does not work when acknowledge an alarm!
  • Cause and action does not work when acknowledge an alarm!
  • Jonas_Brissman
    Jonas_Brissman
‎2018-09-06 11:00 AM
When "Enforce acknowledge response with signature" is marked in the alarm control object the user should have to write in a cause and action when an alarm is acknowledged.
This does not happen.
TAC Vista 5.1.8
In the alarm control object, if you mark booth:
"Enforce acknowledge response" and
It will work but if only "Enforce acknowledge response with signature" is marked it does not work.
If "Enforce acknowledge response with signature" should be used mark also "Enforce acknowledge response" in the alarm control object.