Card format changes are ignored when using RS-485 Readers and SP-RDM2 expander modules

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Card format changes are ignored when using RS-485 Readers and SP-RDM2 expander modules
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • David_Kendrick
    David_Kendrick
  • AdamSteele
    AdamSteele

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1355 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Card format changes are ignored when using RS-485 Readers and SP-RDM2 expander modules

Admiral David_Kendrick Admiral
‎2020-06-30 02:55 AM

Last Updated: Kirk AdamSteele Kirk ‎2021-10-04 09:58 PM

Issue

When trying to alter the Primary or Secondary card formats of Readers wired using RS-485 via RDM2s, any changes at the Server seem to have no effect whatsoever when the reader is then tested.

Product Line

EcoStruxure Security Expert

Environment

  • Card Reader format configuration
  • SP-C
  • SP-RDM2

Cause

A defect has been detected in SP-RDM2 firmware version 1.12.505 whereby format changes made by users via the GUI are not applied to RS-485 wired readers.  Wiegand Readers are unaffected as are any readers wired directly into the SP-C

up1.png

Resolution

SP-RDM2 Firmware version 1.12.545, and above, resolves the issue entirely.
The quickest and easiest way to upgrade this firmware however is actually to first upgrade the SP-C under which the RDM2s are located.

 

1. Update the SP-C to 2.08.923, or greater, using the usual Controller Option.

up2a.png

 

2. Select the correct Firmware .bin file and begin the upgrade (Ignore any Interrupt Error that may be produced).

up4.png

 

3. Check Module Addresses in Security Expert Client to confirm SP-C Firmware has been updated.

up5.png

 

4. Once the SP-C has been updated to 2.08.923, or greater, simply log onto that SP-C's own Web Browser.
Then under the Application Software section there is a new update Module Software option where it is possible to select and update any SP-RDM2 modules connected on that SP-C bus. Once again select the correct .bin file for the firmware and begin the upload.

up7.png

 

Note:  At the time of publication it is possible for an error to also appear at the end of the module upgrade, which suggests that it has not been successful (as seen earlier when updating the SP-C)

Referring back to the Module Addressing page at the Security Expert Client however, it should be possible to see that the SP-RDM2 module has now updated and the system can now be retested.

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (2)
  • Find more articles tagged with:
  • AdamSteele21
  • DavidKendrick20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of