Card Reader not working
  • Card Reader not working
  • Roger_Bently
    Roger_Bently
‎2018-09-06 09:52 AM
Card Reader gets a valid card read but does not unlock the Door.
All versions of I/Net using DPU's 7910, 7920 and SCU 1284.
The Door does not have an Exit Reader but the parameters are set for Anytime.
To resolve the issue, the following steps need to be followed:
  1. Connect to the Controller
  2. Select Controller/Doors
  3. Select the door in question and click on the Modify button
  4. In the Editor, at the Exit Reader, click on the drop down menu and select None from the options.
  5. Click on Okay and close out the Editor.
  • TAC INET
  • 14984