Cannot open admin session Java.net.connect Exception:Connection refused:connect
  • Cannot open admin session Java.net.connect Exception:Connection refused:connect
‎2018-09-06 02:56 PM
Last Updated: Administrator CraigEl Administrator ‎2023-05-22 04:56 PM
When trying to open the admin tool in Niagara R2 Workplace Pro, the following error message appears:
TAC IA Series
This error occurs because the local Niagara service is not running.
  1. Open the console of the desired version
  2. Type admininstall install /start
  3. Now you should be able to log into an Admin tool session.
  • TAC IA Series
Tags (2)
  • 2708
  • CraigEllis23