Cannot log into the I/A Series G3 "localhost" platform

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Cannot log into the I/A Series G3 "localhost" platform
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1226 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Cannot log into the I/A Series G3 "localhost" platform

Picard Product_Support
‎2018-09-06 11:02 AM

Issue

Unable to log in to the localhost, while all user names and passwords associated with the PC have been tried.

Product Line

TAC IA Series

Environment

I/A Series G3 software installed on Windows computer.

Cause

To log into the LocalHost Platform via the I/A Series G3 Workbench, a username and password needs to be used that is defined in the local Administrator's group of the computer on which the software is being used.

Many times, the user accounts on a computer will be Domain based accounts rather than local accounts. The I/A Series G3 software cannot authenticate with Domain based accounts.

Resolution

If logged into the computer as a user that is a member of the Administrator's group, you should be able to create a new user account and assign that user to the Administrator's group.
Below is the procedure for creating a new local user and placing that user in the local Administrator's group on a Windows XP system.

  1. Right-click on the "My Computer" icon and select Manage.
  2. Click on the [+] box in front of "Local Users and Groups".
  3. Click on "Users".
  4. Right-Click in the righthand window and select "New User". A New User window will open.
  5. In the New User window, enter IAAdmin in the User name field.
  6. In the Full Name field enter "IA Admin"
  7. In the Description field enter "Local Administrator for I/A Series R2"
  8. In the Password field enter P@ssword.
  9. In the Confirm Password field enter P@ssword
  10. Uncheck the "User must change password at next login" option
  11. Check the "User cannot change password" option
  12. Check the "Password never expires" option
  13. Click the [Create] button then click [Close] to close the "New User" window.
  14. In the righthand window, right-click on the user IAAdmin and select Properties.
  15. In the IAAdmin Properties window that just opened, click the "Member of" tab.
  16. Click the [Add] button
  17. In the "Enter the object names to select" box, type in Administrators and press Enter.
  18. Click the [OK] button to save the changes.
  19. Close the Computer Management window.

When the Platform is opened and a login is attempted on Localhost, enter "IAAdmin" for the user name and enter "P@ssword" for the password.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 11348
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore